Currently reading:
Maintained or Non-maintained emergency lighting

Discuss Maintained or Non-maintained emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
362
Whilst doing an EICR on a village hall noticed that all emergency lights don't work in the event of power failure.

Been given go ahead to replace. Just had a quick look at the BS5266 but can't find anything on guidance as to when and where you should install maintained lights as opposed to non-maintained.

Can anyone help?
 
It only needs to be lit when the public are in the building, for example a bring and buy sale or a jumble sale etc etc, that's why switching them on with the lights is a good idea and usually specified by engineers when Jobs in these sort of places carried out, Murdocks idea of a combined with a jumper link is a good one
 
Maintained lights can be switched on/off as per normal lighting. Non maintained are for emergency lighting only. The choice depends on whether you need to use the emergency light for normal illumination and emergency, or solely for emergency.

In an emergency you need to light the way to the assembly point and show emergency exits, (door directly to outside) however I don't think this needs to always be lit.

Hope this helps.
 
I hate to say this BUT I think its in the NICEIC Snags and Solutions covering Emergency lighting!

Page 25 of said book "Maintained emergency lights" - BS 5266 recommends a maintained mode of operation for premises where normal lighting can be dimmed or turned off below levels required for identification and illuminance of escape routes.... such as theatre, cinema. It also recommends Maintained for sites where people will not be familiar with the location/premises.

As clear as mud, but I do what I stated in my first answer as it makes sense to me plus if needed you can simply change the mode by refitting the jumper. TLC do the ones I fit.
 

Reply to Maintained or Non-maintained emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock