dlt27
-
- Reaction score
- 26
Sorry title was a bit dramatic, but wanted to get as much knowledge as possible.
I was working at a biomass factory today after they had a fire. Extension leads were apparently the cause.
When doing a test at the db I noticed that L1 phase was at 272v to earth. L2 phase was 222v to earth and L3 phase was 240v to earth. Any phase to neutral was 240v. I then carried out a high loop test on all phases and got between 76 and 80 Ohms.(TNC's/PME).
Due to these readings I went to 11kv transformer that is in the building and done the same test a lv side of panel and was still getting same results. I then took a feed out to earth rods/ earth mat of transformer, but was still getting the same figures. I have got past test results that said ze was 0.2 Ohms a couple of weeks ago.
I also noticed when any circuit is turned off you get 30v from earth to neutral and earth to live. Also rcd's are failing to trip on push buttons.
Just wondered if anyone had an explanation for these findings and if so could you please explain in simpletons terms.
Much appreciated in advance
(I'm guessing a problem with neutral at star point of transformer).
I was working at a biomass factory today after they had a fire. Extension leads were apparently the cause.
When doing a test at the db I noticed that L1 phase was at 272v to earth. L2 phase was 222v to earth and L3 phase was 240v to earth. Any phase to neutral was 240v. I then carried out a high loop test on all phases and got between 76 and 80 Ohms.(TNC's/PME).
Due to these readings I went to 11kv transformer that is in the building and done the same test a lv side of panel and was still getting same results. I then took a feed out to earth rods/ earth mat of transformer, but was still getting the same figures. I have got past test results that said ze was 0.2 Ohms a couple of weeks ago.
I also noticed when any circuit is turned off you get 30v from earth to neutral and earth to live. Also rcd's are failing to trip on push buttons.
Just wondered if anyone had an explanation for these findings and if so could you please explain in simpletons terms.
Much appreciated in advance
(I'm guessing a problem with neutral at star point of transformer).