Currently reading:
Mca and mop for hvac

Discuss Mca and mop for hvac in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Ok, can somebody please explain, with exact code reference and steps/reasons why this works.

MCA 37amps. MoP 60 amps.

Why can I land #8 on a 60amp breaker?

I know theres exceptions in Article 440. Is it in 440.4(b)?

I understand why it would make sense. Larger breaker for inrush. The MCA is already accounting for %125 for ampacity of the wire.

I need help explaining why this is ok to do. Thanks
 

Reply to Mca and mop for hvac in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock