This normally means that the Ze is too high and in applying the test current on the Line earth loop the voltage on the earth will rise above 50V and present danger on the installation.
What result did you get with the two wire method?
If 0.23 then the test should not surely be aborting due to an excessive voltage rise. With my tester I generally use the three wire method for Zs testing when RCDs are present. Not sure why you would be measuring Ze with three probes.
Using three wires for testing the Ze was how I was shown. Is this not correct then?
I think its a 2 or 3 probe test depending on what MFT you have
I have a metrel and I believe it's a 3 wire test but most books or videos Iv watched it's a 2 wire test
Does the tester do a high current test via three wires then? That sounds a bit suspicious!
in all honesty I don't know. Iv had the tester 5 days and ze was the first test I wanted to try with it.
it wouldn't let me do the test with just earth croc and line probe (had the little X on the screen which means the tester isn't ready to do the test) it must be a 3 lead test
The manual is very basic. There is a diagram, that's about as much info as you get.
View attachment 32230
The manual is very basic. There is a diagram, that's about as much info as you get.
View attachment 32230
Before the loop function is Line
I have the new style megger MET also. Select Loop on dial. Then you can toggle with arrow button to left of screen between 2 Hi, 3Lo and 2lo. These are 2 lead High current, 3 lead low current and 2 lead low current.
My tester is the same as this.
The Z loop setting on the dial is a high current test but has a sub setting of Z loop (RCD) which is a low current test.
The Z Line setting is also a high current test for Line-N and Line-Line impedance.
All three tests are described in the manual as three lead tests, and all three tests generate an automatic PFC value.
On the kewtech it describes the hi current test as a L-N test and uses the 1 and 3 connections on the tester (also labelled L and N)
It seems some people don't understand and think it means it is only for testing L-N