I couldn't get a reading, using an MFT1730 tester, using three wires. The tester would start to test but then stop and read >50V. I managed to get a reading using the 2 wire method.

Any ideas?
 
This normally means that the Ze is too high and in applying the test current on the Line earth loop the voltage on the earth will rise above 50V and present danger on the installation.
What result did you get with the two wire method?
 
It should be >50V given its a live test! Not familiar with that particular tester but Ze is a two wire test between disconnected main earth and incoming live.

Edit: just read RB's post and that makes more sense...
 
Last edited:
This normally means that the Ze is too high and in applying the test current on the Line earth loop the voltage on the earth will rise above 50V and present danger on the installation.
What result did you get with the two wire method?

Thanks for the reply. I haven't got the test results to hand, but I think it was 0.23
 
If 0.23 then the test should not surely be aborting due to an excessive voltage rise. With my tester I generally use the three wire method for Zs testing when RCDs are present. Not sure why you would be measuring Ze with three probes.
 
Last edited:
If 0.23 then the test should not surely be aborting due to an excessive voltage rise. With my tester I generally use the three wire method for Zs testing when RCDs are present. Not sure why you would be measuring Ze with three probes.

Using three wires for testing the Ze was how I was shown. Is this not correct then?
 
Not 100% with your particular tester, but my Megger 1552 I use two wire for testing Ze. Zs can be measured with a lower current using three wire method when RCDs are present and to stop them tripping. But this can give erroneous results and it is better to bypass the RCD and use the higher current setting. The manual will be available online mate if you Google it.

Testing Ze is generally close to the origin of the wiring as it were and before any RCDs are present so two wire method will suffice.
 
Last edited:

Reply to Measuring Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
389
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
296
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Hi Guys, just looking for a bit of advise. I am booked up to go on 2391-52 soon, and was looking at using my own tester, Megger1552. It is all...
Replies
5
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock