Discuss Ze readings >2000Mohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

So basically a Zdb is a Zs reading for an outgoing distribution board. Which clears up the misunderstanding with some of the previous comments.

Is there a reason / requirement why the engineer is telling us to disconnect main incoming supplie earthss for every Sub DB?
Not that I can think of. I take it the DBs are supplied by SWA or conduit or trunking with singles? Either way that DB and all the CPCs in it will still be connected to the main earth via parallel paths so taking the earth out will not make much of a difference and like I said the only test carried out with the main earth disconnected is the Ze test.
 
Not that I can think of. I take it the DBs are supplied by SWA or conduit or trunking with singles? Either way that DB and all the CPCs in it will still be connected to the main earth via parallel paths so taking the earth out will not make much of a difference and like I said the only test carried out with the main earth disconnected is the Ze test.

Yes all cables used are SWA.
 
Yes all cables used are SWA.
Your tester is obviously picking up something that's stopping it carry out the test. If you've checked the leads & the tester settings and all is good then you might want to check for loose neutral & earth connections and test for voltage between N & E. If all your there to do is give them Ze/Zs/Zdb results then you've done that, may be people have just made them up in the past. They might need to pay for further investigation.
 

Reply to Ze readings >2000Mohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, I've had an unusual result from taking a Ze at a clients house and wondered what everyones take on it would be: The property is TN-C-S A Ze...
Replies
9
Views
4K
Hi everyone, I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth...
Replies
14
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock