Medical IT Socket-Outlets

Discuss Medical IT Socket-Outlets in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi,

This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current guidance needs updating to clarify this but in the mean time, you should be aware that IT sockets with switches should not be fitted even though they are sold. Having them switched cannot be a derogation because the switches defeat the whole purpose of the IT system, which is to reduce the risk of disconnection (ie an RCD tripping). Life critical medical equipment obviously needs the power as much as possible so medical IT reduces this risk. FYI the control panel is called an IPS because in order to function, the system needs an isolating transformer.

Also, I have seen sockets being sold that do not have the correct "clean" earth link. Basically, the link should be removed if there is a metal back box and kept in if there is a plastic back box. Simple. Why? In a group 2 medical location where IT are fitted, the socket earth pin has a radial connection direct to the location EBB. This should not connect to extraneous (which is connected to the socket screws and back box). If it is a plastic back box, the link is left in and means the screws use the radial equipotential conductor. The problem is - some sockets are sold with a link that doesn't split the screws from the pin - the link terminal is not a link but just one terminal and doesn't help. If the link is out, one of the connections should only go to the socket earth pins.

Hope this helps.
 
Last edited:
I haven't claimed BS7671 to be a statutory instrument, but simply pointed out that it is regulatory as you had incorrectly claimed otherwise.

The terms 'regulation', 'legislation' and 'statutory' are not interchangeable.
i saw a good description recently where it said that BS7671 is directly referenced in other legislation which I haven’t seen before and it better explains my point. Therefore to prosecute, enforcement authorities need to use the actual “other” legislation which directly references BS7671. It is a good point because the additional health guidance isn’t referenced like BS7671.
 

Reply to Medical IT Socket-Outlets in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock