Currently reading:
megaflow

Discuss megaflow in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi guys

Megaflow cylinder

The connections on it are 1 2 3

In the book for an s plan you use 1 and 2 as your cylinder stat

When you turn the programmer on the zone valve is not working and firing the boiler up.

If you open valve manually it works

Now i thought faulty cylinder stat so i done a continuity test between terminal 1 and 2 and nothing

Between 1 and 3 got continuity

So switched cable from 2 to 3 on stat and it seems to work

Anyone had a similar problem
 
Don't run it like that! 1 is the common, 2 is the N/C and 3 is the N/O, if you use 3 instead of 2 to open the 2 port valve you will be heating the mega flow continuously and past it's maximum working temperature.

Now having said that what have you tested and what results did you get?
Have you checked the overheat protection?
Have you checked the temperature the stat is set at?
Is the immersion heater on and so heating the the megaflow up so that it is already warm?
 
Ok, so you have identified that the valve only opens once you have drawn off some of the hot water stored in the cylinder.

Now tell us how you expect the system to operate, and why you think the current operation is incorrect?
 

Reply to megaflow in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top