This forum borks links to the IET site for reasons that are not obvious. However, the important bits from the article (to me at least) are quoted below:Unfortunately that final link did'nt work. Looks interesting. As, firemen are obviously on the front line and have firsthand experience of the real issues
Fires in plastic consumer units - a pattern of fires emerges
Back in 2011, the Fire Investigation Team identified an increase in the number and severity of fires involving consumer units. The team started looking carefully at the cause of those fires and established that there were issues with high resistance connections, where cables were not secured properly. This had the potential to lead to localised heating, arcing and, in some cases, to fires. There was also an emerging problem due to a large batch (over 1 million units) of non-compliant miniature circuit breakers (MCBs), which were subject to a product recall and which could also fail catastrophically.
Severe fires
The team were also seeing more fires that were spreading beyond the consumer unit and putting people’s lives at risk. Through a careful process of laboratory examinations and tests at Brigade consultant scientists Bureau Veritas, concern was raised about the flammability of the plastic enclosures of consumer units. Working closely with Electrical Safety First, more extensive tests of five plastic consumer units from different manufactures were carried out in 2012. These tests gave significant cause for concern due to the intensity of the fire and the levels of toxic smoke produced.
Location, location, location
A significant cause for concern when a consumer unit becomes involved in a fire is that it is commonly located on an escape route, for example, under the stairs or behind the front door. When this is combined with the fairly usual situation of coats, outdoor wear and other household items being stored nearby, once the fire starts, it often develops very quickly. London Fire Brigade was becoming extremely alarmed at the number of injuries occurring at such fires and the need for people to be rescued as they became trapped when the escape route was involved in fire.
A way forward
Working with Electrical Safety First, industry body BEAMA and other stakeholders, the process of presenting evidence for change began. A JPEL/64 project group was set up and ‘robust’ discussions about possible changes to BS 7671 (the Wiring Regulations) continued over several months.
Representatives from the Department of Communities and Local Government (DCLG) attended and raised concerns about possible changes. As a result of these concerns, DCLG commissioned independent tests at the Building Research Establishment (BRE). BRE tested two plastic and two metal consumer units and the subsequent report appeared to strongly support the need for change, stating:
“Both plastic consumer units caught fire and their casings became involved in the fire”… … “Both metal consumer units contained the fire within the unit” (Source: BRE report BD2890)
Also, some manufacturers ran their own tests, the outcomes of which again demonstrated the need for change. This led to a new regulation to be included in Amendment No. 3 to BS 7671, effectively requiring consumer unit enclosures in domestic households to be manufactured from non-combustible material (such as steel) or to be enclosed in a cabinet or enclosure constructed of non-combustible material. This new regulation is a welcomed step-change improvement in fire safety.