this however is exactly what i want to avoid if at all possible
You would prefer to have a defective cable / joint remain live and in service without knowing the nature or extent of the defect?
Discuss missing lighting cpc in the UK Electrical Forum area at ElectriciansForums.net
this however is exactly what i want to avoid if at all possible
no that is not what i was suggesting, as a C1 failure it has to be resolved, my preference is for a more elegant solution than his suggestion, tacking in an extra wire via external trunking. If a cpc is derived from another cable then the induced voltage collapses and the circuit is no longer live and is safe, is it not ?You would prefer to have a defective cable / joint remain live and in service without knowing the nature or extent of the defect?
the problem for me is how many qualified people do I need to employ until I find one who is capable of faultfinding. If the conductor can be shown through measurement to be o/c in the leg from the consumer unit, and this cable is largely inaccessible then there are only two options open 1a) lift all the carpets, floor boards, buried trunking and run a new cable to the first ceiling rose in the loft 1b) run a new cable in external trunking to the first ceiling rose in the loft 2) take a cpc from somewhere adjacent to the first ceiling rose in the loft. What would you suggest to your customer if this was the 1 time out of 10 where it could not be readily rectified ?I would be using using the earth from another circuit as a last solution. Someone needs to establish where the problem is as nine times out of ten it can be rectified. I suspect you are wasting your time with this electrician.
no that is not what i was suggesting, as a C1 failure it has to be resolved, my preference is for a more elegant solution than his suggestion, tacking in an extra wire via external trunking. If a cpc is derived from another cable then the induced voltage collapses and the circuit is no longer live and is safe, is it not ?
the proposal to use another cpc is not mine it is the suggestion of the author of the fail certificate, I am simply suggesting a less obtrusive version of his suggestion. If the conductor has been partially severed and is now live would an insulation test L/E indicate >500Meg ? The electrician has confirmed that the voltage present on the fascia screws is induced, if it really was line voltage then would not the connection of an cpc from elsewhere to this potentially partially severed cpc cause the MCB to trip ?No, not necessarily. The CPC of a cable does not suddenly go open-circuit by itself. Something is significantly wrong with that cable run, but you don't know what. You know only the symptom that the EICR has thrown up, i.e. open-circuit CPC, and you propose to alleviate that symptom by providing an alternative CPC. Anything else that is wrong will remain live and in service.
As I said back in post #6, the cable might have been partially severed by a screw or nail which is now live. Or it might contain a thoroughly defective joint made by an unskilled person using sellotape, of which one of the three cores has so far given way. Or it might have been ripped to shreds by catching on a Skil saw when somebody was cutting floorboards, and now the bare length of line conductor is resting against a non-extraneous gas pipe. You don't know whether any of these apply to you, only that the broken CPC has alerted you to a problem with the cable. Do you intend to ignore any other ramifications once your CPC is reconnected to the MET?
If the conductor has been partially severed and is now live would an insulation test L/E indicate >500Meg
Thanks for that referenceOn the question of which regulation states that you cannot use a CPC from one circuit to add a CPC to a different circuit, you will not find any such regulation. On the contrary 543.1.2 and onward shows the requirements for where two or more circuits share the same CPC. So in some circumstances it might be perfectly acceptable.
However, as Lucien and others have pointed out, this would not be an appropriate solution to the "missing" CPC in your situation. You would only be masking the symptoms, not correcting the fault.
A bit like taking painkillers to treat a bleeding artery. You need to find the problem and repair it.
I appreciate your engagement. Thanks.The CPC is completely severed. I'm not so worried what that might or might not be in contact with, as one side is already earthed and the other side is going to get earthed. It's the other bits that might be involved. What was the insulation reading from line to shelf bracket?How about line to shower-curtain rail? (we had one of those some years back, the rail was solidly live from where a fixing screw had penetrated a cable.)
I won't bother trying to convince you any further.
Lucian what do you use to Inject a tone into the cable?2. Inject tone into cable and search with tracer along likely routes. If it can be found at least at a few waypoints, estimate total length along that route.
Reply to missing lighting cpc in the UK Electrical Forum area at ElectriciansForums.net