Currently reading:
New build outside light

Discuss New build outside light in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
32
Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
 
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
 
Essex, what happens in my son,s case, when he is changing the existing light fitting for a different one. Is it just tough luck, you will now need to run in your own earth now ?
Seems a bit shabby for a new build.
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
The luminaire is an outside light mounted on a rendered wall
 
Essex, what happens in my son,s case, when he is changing the existing light fitting for a different one. Is it just tough luck, you will now need to run in your own earth now ?
Seems a bit shabby for a new build.

I agree it is a bit crap and there may be a specific regulation that states all cables shall be terminated correctly somewhere in the regs but someone else may be able to assist there. That is of course if the CPC has just been cut off short - which is likely.
 
It happens a lot in here. ;-).

Class 2 equipment does not rely on ADS (Automatic Disconnection of Supply) for fault protection so 411 is not applicable.
the equipment may not need a cpc, but the cable to it does.
 
I agree it is a bit crap and there may be a specific regulation that states all cables shall be terminated correctly somewhere in the regs but someone else may be able to assist there. That is of course if the CPC has just been cut off short - which is likely.
Yes I will check that next time I,m up at their house. We babysit once a week, they live 55 miles away from uf !
 
In case someone drills a nice hole into the cable in the wall...........

I don't follow. There is no guarantee that someone would hit the CPC and live conductor. The circuit would also still disconnect if the live and neutral was hit.

There are other things in place to prevent electric shock from drilling.
 
I don't follow. There is no guarantee that someone would hit the CPC and live conductor. The circuit would also still disconnect if the live and neutral was hit.

There are other things in place to prevent electric shock from drilling.
And what if they didn't hit the live and neutral just the live and earth.......or in your case just the live because there is no earth........
 
And what if they didn't hit the live and neutral just the live and earth.......or in your case just the live because there is no earth........

To be fair, I experienced a fault, where a previous home owner had nailed a dado rail to a wall, nicking just one strapper in a tw&e. Livened up the whole wall for the next 10 years, depending on which way the landing light was switched.
 
To be fair, I experienced a fault, where a previous home owner had nailed a dado rail to a wall, nicking just one strapper in a tw&e. Livened up the whole wall for the next 10 years, depending on which way the landing light was switched.
Nice.......but I bet he had an earth.....seems that Essex is quite prepared to run a cable to an external light without one
 
Why would a new installation be installed in such a way, so that the potential unknown owner would have to install Class 2 luminaires?

To coin previous catch phrases, although not impossible, just very unlikely.

I am not doubting there stupidity, just debating whether it is actually against BS 7671.
 
Nice.......but I bet he had an earth.....seems that Essex is quite prepared to run a cable to an external light without one

Whether it had an earth or not is irrelevant as in the example it counted for nothing.

I would be happy to run a cable to any double insulated electrical equipment with no earth as it is specifically stated that an earth is not required. Would I do it in the ops case - no.
 
I am not doubting there stupidity, just debating whether it is actually against BS 7671.

Ok, but it doesn't help the OP; we all know - unless the particular installer had gone wibble that day - that there will be a cpc at this particular point in question. OP just has to look for it. Now he knows this is the normal accepted way of doing things.
 
Getting a bit complex for the OP (me) Is there no definitive then, on whether a CPC should be taken to an external class 2 luminaire on a new installation ?
On a new installation then yes of course a cpc should have been ran to the light.
Irrelevant if it’s class 2 what if it was to be changed in the future to a class 1?
Can’t be done because some numpty cut the cpc out?
The regulations require a cpc to each point.
You are not using the protective measure double and reinforced insulation as it’s prohibited on a domestic installation.
It’s the same principle as wiring to a light switch which is plastic,why wouldn’t you install a cpc to it? What’s worse is, if it’s a twin and cpc cable ,the cpc has been cut off!
Hope this helps :)
 
Getting a bit complex for the OP (me) Is there no definitive then, on whether a CPC should be taken to an external class 2 luminaire on a new installation ?

It will have one there, unless the contractor lost his head; you just don't need to earth a Class 2 fitting, in fact you must not (manufacturers instructions taken into account).

So when you go back to your sons house, locate the earth & connect it to your Class1 fitting in an orderly fashion.

Ignore the heated debate, it will be there & you will find it. However you will need to verify its continuity.

PS if its not there, sue the ba****ds :)
 
Ok, but it doesn't help the OP; we all know - unless the particular installer had gone wibble that day - that there will be a cpc at this particular point in question. OP just has to look for it. Now he knows this is the normal accepted way of doing things.

I think it does help as the op is looking to go back to the builder. If there is no Reg break then he cannot do that.
 
I think it does help as the op is looking to go back to the builder. If there is no Reg break then he cannot do that.
There is a regulation break.
411.3.1.1.
Regardless if the light is class 2, the protective measure double or reinforced insulation can’t be used on a domestic installation.(yes by nature the light doesn’t require a connection to earth).
By the nature of the light fitting being class 2,it’s not inherently dangerous at the moment but it does not comply
 
Last edited:
essex you've made you point, why do want to keep making it?

Us house bashers have nothing in our vans besides crisp packets mucky dees waste, and twin & earth cable.

I am not sure why you are getting so upset. I was enjoying the debate but I will leave it if you would prefer. I would not want anyome thinking this is a forum for debating or anything like that.
 

Reply to New build outside light in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock