Iona222

Trainee
Reaction score
41
I'm working with my friend a sparky. He changed the consumer unit.

Before hand I checked all circuits for continuity and done quick eicr, everything was OK.

Now with the new board on were getting a neutral fault showing on socket ring. Funny thing is the rcd manual test button isn't working. On the rcd coving the said ring. You think it could be something to do with this why showing a fault on ring. Thank you.
 
Have you IR tested that circuit, either as part of checks before new board, or since the problem emerged?
Have you tried all circuits off and done an RCD test?
Is it a dual-rcd board - have you tried the circuit the other side - see if the problem moves?
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
You asked me what im thinking.

The spark has extended the cpc using the wrong size cpc causing more fault current to go through the neutral. Causing the test button not to work.
If I change the cpc to the correct size the fault current will go to earth, the neutral will be what it should be, the test button will work.
Thats what I think.

Thats what ill be doing 1st thing Tuesday
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

Assuming the earthing conductor should have been 16.0 replacing a short section with 10.0 will have a negligible effect. You have a neutral to earth fault on the ring final so why would a reduced earthing conductor change this.
No larger cpc that is required, if you read what I put he's put 4mm cpc on a circuit that should be 1.5mm. Does the cpc not need to be the correct size.
 
I read that you can get a error from neutral to protective earth if the cpc is oversized.

the extended cpc has nothing to do with it. you have a N-E fault on the ring circuit which is inhibiting thr RCD. i don't know the theory behind this but i've had it a couple of times.
OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
 
OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
Its not the "oversized" cpc. You've been told that. Have you measured earth leakage from the circuit whilst energised? Have you done an IR test of the circuit to the MET, have you ensured the neutrals are in the correct bar. Have you split the circuit in half and tried energising 1 leg?
 
Now with the new board on were getting a neutral fault showing on socket ring.

OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
In your OP, you say there is a neutral fault. Later you say the circuit has passed IR. Please can you explain this, so we are better placed to advise?
 

Reply to New consumer unit install issue. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock