I'm working with my friend a sparky. He changed the consumer unit.

Before hand I checked all circuits for continuity and done quick eicr, everything was OK.

Now with the new board on were getting a neutral fault showing on socket ring. Funny thing is the rcd manual test button isn't working. On the rcd coving the said ring. You think it could be something to do with this why showing a fault on ring. Thank you.
 
Have you IR tested that circuit, either as part of checks before new board, or since the problem emerged?
Have you tried all circuits off and done an RCD test?
Is it a dual-rcd board - have you tried the circuit the other side - see if the problem moves?
 
Have you IR tested that circuit, either as part of checks before new board, or since the problem emerged?
Have you tried all circuits off and done an RCD test?
Is it a dual-rcd board - have you tried the circuit the other side - see if the problem moves?
No haven't tried these, will do.
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
You asked me what im thinking.

The spark has extended the cpc using the wrong size cpc causing more fault current to go through the neutral. Causing the test button not to work.
If I change the cpc to the correct size the fault current will go to earth, the neutral will be what it should be, the test button will work.
Thats what I think.

Thats what ill be doing 1st thing Tuesday
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

Assuming the earthing conductor should have been 16.0 replacing a short section with 10.0 will have a negligible effect. You have a neutral to earth fault on the ring final so why would a reduced earthing conductor change this.
No larger cpc that is required, if you read what I put he's put 4mm cpc on a circuit that should be 1.5mm. Does the cpc not need to be the correct size.
 

Reply to New consumer unit install issue. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
552
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
670
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
651
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock