Hello Guys,

I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all, to see if I have got this right in term of cable selection and load, or if anyone can suggest another way of doing this…

The Office will use the following load, I have rounded all amounts up to be safe.

3 x 1.5 kw heaters = 4500w = 20Amps

8 x 50w down lights = 400w = 2 Amps

4 x computers = (allow 250w per machine) =1000w = 5 Amps

Possible additional usage (microwave/printer/phone charge/fan etc) allow approx 1000w = 5amps

TOTAL AMPS = 32



I plan to install a 10mm PVC multi-core cable from Fuse board, (Protected by a 40 or 45 amp MCB or RCBO) through the house, until outside, then change to 10mm SWA up to the new installation. (Approx 15 meters away)

A new garage board will be installed with rcd in the new office, protecting the relevant new circuits.

(It is yet to be decided if client wants to have a new main fuse board in the house or install a separate unit fed from the Henley block.. The old fuse board is re-wireable fuses and non-rcd. I believe the earth arrangement is PME at this stage.



I would like your opinions and suggestion please

Thanks!



 

Reply to New garden office, Cable selection and method...? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top