srl-8

Hello Guys,

I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all, to see if I have got this right in term of cable selection and load, or if anyone can suggest another way of doing this…

The Office will use the following load, I have rounded all amounts up to be safe.

3 x 1.5 kw heaters = 4500w = 20Amps

8 x 50w down lights = 400w = 2 Amps

4 x computers = (allow 250w per machine) =1000w = 5 Amps

Possible additional usage (microwave/printer/phone charge/fan etc) allow approx 1000w = 5amps

TOTAL AMPS = 32



I plan to install a 10mm PVC multi-core cable from Fuse board, (Protected by a 40 or 45 amp MCB or RCBO) through the house, until outside, then change to 10mm SWA up to the new installation. (Approx 15 meters away)

A new garage board will be installed with rcd in the new office, protecting the relevant new circuits.

(It is yet to be decided if client wants to have a new main fuse board in the house or install a separate unit fed from the Henley block.. The old fuse board is re-wireable fuses and non-rcd. I believe the earth arrangement is PME at this stage.



I would like your opinions and suggestion please

Thanks!



 
Hello Guys,

I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all, to see if I have got this right in term of cable selection and load, or if anyone can suggest another way of doing this…

The Office will use the following load, I have rounded all amounts up to be safe.

3 x 1.5 kw heaters = 4500w = 20Amps

8 x 50w down lights = 400w = 2 Amps

4 x computers = (allow 250w per machine) =1000w = 5 Amps

Possible additional usage (microwave/printer/phone charge/fan etc) allow approx 1000w = 5amps

TOTAL AMPS = 32



I plan to install a 10mm PVC multi-core cable from Fuse board, (Protected by a 40 or 45 amp MCB or RCBO) through the house, until outside, then change to 10mm SWA up to the new installation. (Approx 15 meters away) What type of cable would this be? would depending on the cable and erection method, need RCD additional protection. Is the CPC the same size as the LIVE conductors?

A new garage board will be installed with rcd in the new office, protecting the relevant new circuits. If the multi core cable in the house needs additional 30mA protection will you have an issue with RCDs in series

(It is yet to be decided if client wants to have a new main fuse board in the house or install a separate unit fed from the Henley block.. The old fuse board is re-wireable fuses and non-rcd. I believe the earth arrangement is PME at this stage.



I would like your opinions and suggestion please

Thanks!

Will this office have services, such as a bathroom and therefore a water supply, is the construction of the building metallic at all, What type of earthing system do you have?
 
I would probs install 100MA RCD at House end and 30Ma RCD at garage end. This should allow garage to trip first, and not the house RCD
 
The cable going through the house, what kind of cable is it, and if is buried anywhere will you need to give it RCD protection?

If it is T + E and 10mm your CPC will be 4mm and your SWA CPC will either 10mm extra core or the armour, will that 4mm if T +E be man enough?
 
Is it feasible to take the SWA right back to the CU ?


No Andy, it is impossible to run the SWA back to CU, I will have to make a connection somewhere on the outside wall etc.

cable for inside the house will be same as typical shower cable 10mm twin & earth
Cable for outside 10mm SWA
 
as above comments, and, if using 10mm T/E in the house, run a separate 10mm earth with it.
 

Reply to New garden office, Cable selection and method...? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
944
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
771
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock