Currently reading:
new washing machine trips 3 phase rcd incomer

Discuss new washing machine trips 3 phase rcd incomer in the Australia area at ElectriciansForums.net

G

graham1

Hi Chaps,
Got called to an interesting one today, customer has bought a new miele washing machine for a farm building. It is a straight swap for an older machine, trouble is during its cycle it trips the 3 phase rcd 30ma incomer. The socket it is connected to is fed from a single phase breaker connected to L1. Funny thing is if you plug the machine into a socket on a different phase all is ok. Have ramp tested the rcd from both circuits & get the same results (trips around 24mA) but it only evers trips when using first phase!
Any ideas how each phase could affect the rcd differently?
Thanks!
 
Probably there is more leakage on L1 phase from other circuits on the same phase, be it natrual or otherwise. That's what you need to find out, by your fault finding exercise...
 
Last edited by a moderator:

Reply to new washing machine trips 3 phase rcd incomer in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top