graham1

Hi Chaps,
Got called to an interesting one today, customer has bought a new miele washing machine for a farm building. It is a straight swap for an older machine, trouble is during its cycle it trips the 3 phase rcd 30ma incomer. The socket it is connected to is fed from a single phase breaker connected to L1. Funny thing is if you plug the machine into a socket on a different phase all is ok. Have ramp tested the rcd from both circuits & get the same results (trips around 24mA) but it only evers trips when using first phase!
Any ideas how each phase could affect the rcd differently?
Thanks!
 
Probably there is more leakage on L1 phase from other circuits on the same phase, be it natrual or otherwise. That's what you need to find out, by your fault finding exercise...
 
Last edited by a moderator:

Reply to new washing machine trips 3 phase rcd incomer in the Australia area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
622
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
10
Views
797
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock