highspark

Done a board change today.

Kitchen Sockets on RCD1, Up sockets on RCD2. Both rings.

When energised RCD1 tripped. When I removed the neutral of the Up sockets on RCD2, the Kitchen Ring & RCD1 did not trip. As soon as I put neutrals back in on RCD2 side. RCD1 trips.

Thought there may be a borrowed neutral or got legs mixed up, so decided to put both circuits on the same RCD and neutral bar. Still Tripped!

Removed all appliances from Circuits - still tripped.

Next replaced both RCD's still tripped. Scratching my head off!!

its a hard one to explain. Basically when all conductors of both rings are connected the RCD just trips. If I remove the up sockets completely the kitchen sockets are fine and vice versa! It's only when all conductors are connected!!

Is is there an interconnection somewhere between these two circuits?

the only work they've had carried out is a new kitchen 4 years ago and a new boiler with a y plan system 3 years ago. I'm guessing there's been an interconnection made at those times!
 

Reply to Nightmare fault!! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top