Just speccing a job for tomorrow - simple 3ph immersion supply at 12kW. Supply to be constantly on, using the immersion temp stat for control (by request....) via a local isolator. (Have suggested future improvements with timers, stats, contactors etc but for now it's just this)
So that's basically 17A per phase, table 4D4A says that 4mm NYY-J will be absolutely fine at 34A max on some tray, it's only about a 15m run max from the board. C20 in the board, job done. It just all sounds a bit lightweight though for a 'constantly' running 3ph heating supply??