Currently reading:
NYY-J sizing

Discuss NYY-J sizing in the UK Electrical Forum area at ElectriciansForums.net

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
6,461
Just speccing a job for tomorrow - simple 3ph immersion supply at 12kW. Supply to be constantly on, using the immersion temp stat for control (by request....) via a local isolator. (Have suggested future improvements with timers, stats, contactors etc but for now it's just this)

So that's basically 17A per phase, table 4D4A says that 4mm NYY-J will be absolutely fine at 34A max on some tray, it's only about a 15m run max from the board. C20 in the board, job done. It just all sounds a bit lightweight though for a 'constantly' running 3ph heating supply??
 
17A is 17A. If it were bare MICC ref method E/F/G it would be well in on 4L1.5 and just in on 4H1 (although disallowed as a 1mm² power circuit). 12kW is only six pairs of CP62s. Remember those?

I don't like MCB ratings close to long-hour loads, some manufacturers recommend 80% or so to prevent premature MCB ageing. Could you use a B25? If not, can you put blanks either side?
 
Last edited:
17A is 17A. If it were bare MICC ref method E/F/G it would be well in on 1.5mm² and almost in on 1.0 (although disallowed for being a power circuit). 12kW is only six pairs of CP62s. Remember those?

I don't like MCB ratings close to long-hour loads, some manufacturers recommend 80% or so to prevent premature MCB ageing. Could you use a B25? If not, can you put blanks either side?
lol - I do indeed not only remember with fondness (see my profile pic!) but also can't wait to get back out using them again (in the generic sense) - and yes, I take your point. As for the MCB, it'll be a case of if I can source a C25 off the shelf today (I have a C20 in stock already) but it's going into an almost empty Hager board anyway so loads of ventilation.
 
Groan.... can't find 4mm 5c NYY locally anyway so it's a choice of 4mm SY (which in fairness would be fine, I just don't like it) or 6mm H07 which just seems a waste of copper.
 

Reply to NYY-J sizing in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top