- Reaction score
- 17,163
I got one of these ready built consumer units for my father in laws EV install. Got the cables run in, mounted the charge point etc…. Then took the cover of this.
I don’t know, maybe still peed off standing in the rain all afternoon… but this got me confused.
Left to right, RCD, 32A MCB, SPD
Incoming feed into N and 2 of the RCD…. But where do I take the cable out to the charge point?
Top N of the RCD goes to SPD, 1 of the RCD into top of MCB. Out bottom of MCB into SPD.
So logically, my outgoing needs to be top N of RCD, and Live from the bottom of the MCB… both in beside a ferruled linking cable.
Compared to a regular consumer unit, everything’s upside down.
I don’t know, maybe still peed off standing in the rain all afternoon… but this got me confused.
Left to right, RCD, 32A MCB, SPD
Incoming feed into N and 2 of the RCD…. But where do I take the cable out to the charge point?
Top N of the RCD goes to SPD, 1 of the RCD into top of MCB. Out bottom of MCB into SPD.
So logically, my outgoing needs to be top N of RCD, and Live from the bottom of the MCB… both in beside a ferruled linking cable.
Compared to a regular consumer unit, everything’s upside down.