OSG, bonding plastic pipes etc etc

Discuss OSG, bonding plastic pipes etc etc in the UK Electrical Forum area at ElectriciansForums.net

magnoliafan89

-
Esteemed
Arms
Reaction score
540
Hi all

Having a thumb through the OSG and on section 4.5 Main protective bonding of plastic services, it says there is no need to bond an incoming service of the service pipe is plastic....thats kind of a given....my struggle lies on the next page;
"Where there is a plastic incoming service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that anu metallic pipework within the building is not introducing Earth potential"

Is there a way of determining if there could be an earth potential?
I may be asking a really simple question and be mortified by stupidity but at this moment in time im lost. If a house is supplied with plastic services incoming but then throughot the dwelling it is metal pipes...whats the score with bonding?

Cheers in advance
 
There is a cinema event coming up at 40 cinemas over the country in The next month.
@camerabloke can bring his popcorn!

Yes, and they are (Certsure) spending my money, hiring the Faraday Lecture Hall, uploading the conference to satellite, and pinging it to selected cinemas, invited architects and all sorts. £5 a head. Instead of them larging it up, they'd please me and a lot of others by reducing their fees.
 
It’s so we are all singing from the same hymn sheet, I’m near the front as a soprano (the high voice one not the murderous kind).
At least they are charging per head to recoup some of your money - I’ve been told to pay you directly.
Can I have your bank details and PIN code.
Yes, and they are (Certsure) spending my money, hiring the Faraday Lecture Hall, uploading the conference to satellite, and pinging it to selected cinemas, invited architects and all sorts. £5 a head. Instead of them larging it up, they'd please me and a lot of others by reducing their fees.
 
wasnt there talk in the 18th draft that water/gas pipes might not need to be bonded in the new edition given the amount of plastic used in the supply outside to the property?
i vaguely recall something about it. of course if you start adding plastic in between existing parts of copper then it makes the issue irrelevant for a large part of the install.
 
It’s so we are all singing from the same hymn sheet, I’m near the front as a soprano (the high voice one not the murderous kind).
At least they are charging per head to recoup some of your money - I’ve been told to pay you directly.
Can I have your bank details and PIN code.

What I can't quite understand, is their events like Live South 2018, are £29+vat for members and £49+vat for non members, populated with sponsors. Whereas the Faraday Theatre lecture, that must be costing a Kings ransom, no sponsors etc, is just £5+vat to anyone.

Go figure that. Don't I (Certsure) look important now. :mad:
 
The thing i think of if say in a loft or under the floor... A rat munches on a cable and it lays on a hot pipe... Perfectly reasonable scenario... Well if we all stop bonding the water at point of entry as seems to be the case, and more so with the 18th coming... Whats to protect us from the pipework becoming live in this situation
Nothing.
The case you are thinking of is a failure of both insulation and sheathing, which is not intended to be protected by bonding nor earthing.

Bonding protects an equipotential zone from a potential being introducted from outside the zone relative to DNO earth (usually local earth). Such means of introduction are called extraneous conductive parts.
There is also earthing, which protects against faults inside class I equipment and involves connecting the casing of such equipment back to the DNO earth to disconnect the supply in the case of a fault inside. Likewise for single insulated wires elsewhere and metal cased switchgear.

Both bonding and earthing add a very small element of danger due to the connection of conductive parts to the electrical installation which may lift them above local earth.
Not earthing your butter knives in case someone uses them to poke the bread from the toaster is an example to the contrary about danger from not earthing the mentioned pipes.
Indeed, in every case, having any conductive parts whatsoever in the vicinity of an electrical installation adds an element of danger, so plastic pipe and timber studwork is the way forward if that small level of risk is not acceptable.
 
Some of the above posts seem to miss the point that if internal metal pipework is connected to metal taps (etc), then it needs to be earthed. If the 22k ohm or the 5 Meg ohm pipeworks got shorted to the phase conductor then the 22k would trip the RCD (if fitted on old installations) but the Meg ohm pipework would sit at 230 volts - a real hazard. As I understand the situation, bonding is only not required when all touchable metal parts (taps, sinks, radiators) are only connected by insulated fittings (or pipework). Otherwise it should be bonded. Proper bonding at the boiler (water, gas or oil pipe) is probably best.
 
Some of the above posts seem to miss the point that if internal metal pipework is connected to metal taps (etc), then it needs to be earthed.
not sure about needs, I specifically addressed that in detail with explanation and example
If the 22k ohm or the 5 Meg ohm pipeworks got shorted to the phase conductor then the 22k would trip the RCD (if fitted on old installations) but the Meg ohm pipework would sit at 230 volts - a real hazard.
likewise with your teaspoons, knives, wedding ring, keys, door handles, cordless drill, chisels

I mentioned in my previous posts that the only way to ensure safety is to not have anything conductive but I'd have to go further and recommend wearing a full metal chainmail suit to create your own personal equipotential zone.
 
Conductive parts in the vicinity of the electrical installation but not part of it are not required to be earthed because the regulations require that the risk of electrical contact is addressed and minimised.

An exposed conductive part, i.e. one which is an integral part of the electrical installation, accessible to touch and may become live under fault conditions, is required to be earthed.

Bonding would be required to conductive parts likely to introduce an external potential into the installation.

Neither of the above two cases is applicable to metal parts accessible to touch that are not part of the electrical installation.
 
Some of the above posts seem to miss the point that if internal metal pipework is connected to metal taps (etc), then it needs to be earthed. If the 22k ohm or the 5 Meg ohm pipeworks got shorted to the phase conductor then the 22k would trip the RCD (if fitted on old installations) but the Meg ohm pipework would sit at 230 volts - a real hazard. As I understand the situation, bonding is only not required when all touchable metal parts (taps, sinks, radiators) are only connected by insulated fittings (or pipework). Otherwise it should be bonded. Proper bonding at the boiler (water, gas or oil pipe) is probably best.

I thought the current advice was that kitchen sinks most definitely do NOT require bonding.

Seems a bit counter-intuitive I'll grant, but that is my understanding of the latest solid advice on the subject.
 
My brother-in-law is a Gas Safe engineer and he is adamant that plastic gas pipes coming out of the ground have to be converted to metal (usually barrel) before they emerge - the reason for this being that plastic is not considered mechanically, UV, or thermally (think extraneous applied heat from the sun or open flames (well, it is gas pipe!)), robust enough.

Thus the (metal) gas meter and therefore any metal pipework connected to it on the consumer side will be at local earth potential.

MDPE pipe is only UV resistant in black. Potable water is blue - but for internal or underground use only, and gas is always yellow.
 
I think your 'current advice' was actually a few decades back.
Really?

Happy to be corrected, but I am pretty sure that I saw this on one of the web sites like voltimum.co.uk in recent months...?

Here is just one reference:

IET Forums - Kitchen sink bonding - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=32335

but I'm sure I have seen it elsewhere as well.
 
I was having a butchers round some new show homes recently. On the CU was a printed label, that said words to the effect, water service plastic, internals plastic, therefore water not bonded. Don't know why they chose to share that with everyone?
They've probably been pulled in the past by a jobsworth from an office so did it to save about a million emails and phone calls to try and explain why.....been there had that
 
Really?

Happy to be corrected, but I am pretty sure that I saw this on one of the web sites like voltimum.co.uk in recent months...?

Here is just one reference:

IET Forums - Kitchen sink bonding - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=32335

but I'm sure I have seen it elsewhere as well.

Have you read your link?
 
Have you read your link?
Yes - briefly reminded myself of what it said again today but first read it ages ago.

I am guilty of too broad a brush stroke with the "NOT" in my first post. Of course, it should be "may not" - the possibility of metal waste pipes and all that should be taken into consideration.

(I love a bit of pedantry - as long as it is not me on the receiving end of it of course. :) )
 

Reply to OSG, bonding plastic pipes etc etc in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock