Spengler

DIY
Reaction score
1
Hi,

I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I can’t get it to work. The LED lights come on so it definitely getting power. But both 3 pin plug sockets refuse to work. I have read and re-read the instructions it came with and I have definitely fitted it correctly.

I thought it was the socket itself so I went out and bought another one which also has LED lights on and after fitting I have exactly the same situation.

I have checked the consumer unit and all seems fine. The outdoor sockets are on their own trip switch.

Any ideas on what I might be doing wrong?

FYI the previous outdoor socket worked fine.
 
What are you using to test the socket?
I am plugging in an iPhone charger to the 3 pin plugs and seeing if it will charge my phone. I’ve also plugged in other electrical devices and have the same problem. The LEDs are on but the 3 pin plugs just won’t work.

I also removed the whole socket and put an electrical test screwdriver on the live wire and it lit up showing it is live.

Is there another way I should be testing it?
 

Attachments

  • IMG_4046.jpeg
    1,000.7 KB · Views: 51
  • IMG_4047.jpeg
    350.7 KB · Views: 53
  • IMG_4048.jpeg
    457.6 KB · Views: 51
If that cable is connected the same at the other socket then the armour is not earthed and it needs to be.
Nothing is shouting anything wrong and the connections aren't great. Not impossible the socket is faulty.
 
Could be a N - E reversed at the other end ?

But still wouldn't explain why the old one worked and the new one now doesn't
 

Reply to Outdoor electrical socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top