R
Richard Revell
Been a while since I done a PAT test on a 20meter extension cable and kinda forgot how to do it. The calculation I mean.
Discuss Pat tester not long passed 6 months need to clarify the Extension lead test in the The Welcome Forum area at ElectriciansForums.net
Welcome to the forum
Assuming you are talking about earth resistance, just look up resistances of lengths of cable in the COP and multiply e.g 1.5mm² is 13.3mohms/m so a 20m length would be 13.3*20/1000 = 0.266 ohms
therefore earth resistance should be 0.366 ohms or less.
Reply to Pat tester not long passed 6 months need to clarify the Extension lead test in the The Welcome Forum area at ElectriciansForums.net