Search the forum,

Discuss periodic inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

K

K&L_Electriccal

We did a 5 yearly periodic inspection report on a care home a few week ago that was built in “august 2005” the only RCD protected circuits we found was for the out side sockets, none of the sockets inside had any so what would you guys recommended for this if any,

Cheers lee
 
I would think it is a 4, however, you should code any socket that can "reasonably" be used for outside appliances as a 2 which are not RCD protected.
 
Don't we just love the codes no RCD protection for sockets well in the ESC guide it states it should be a 2 and gives an example of sockets in a TT system. In the OSG example it also gives it a 2 for just sockets in general.

Personally I also think it should be a 2 requires improvement. Did you find any of the bathrooms or shower rooms with RCD protection? and if they didn't have it, and needed it, what did you code them?
 
ESC guide states a 4 for a socket that is unlikely to supply equipment outdoors and is not in a bath or shower. The op stated that outdoor sockets have RCD protection.
 
It a code 1 lol thought id throw that one in did an inspection on friday , flat screen TV on the side of the bath plugged into an extension lead which was in a socket that wasnt RCD protected .... and guess what i had no camera with me why does it always happen no normally a code 4
 

Reply to periodic inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
8K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock