Knobhead
Sounds like fun Tony, any oh **** moments or did it all turn on ok?
There's been a few "Why did I do that?" moments.
The best bit was being accused of being drunk. The above switchroom and the great white chief showed up. He noticed incomer 1 was BYR, incomer 2 RYB. Off he goes to the engineering manager saying I must have been drunk to make such a stupid mistake.
At least he had the decency to come back and apologise.
The bottom line, even if the LV intake is reversed so long as the system follows the same rotation throughout you won’t get a problem.
Note, I did say LV, once transformers get involved then there’s phase shift to take in to account. I’ve seen some glorious balls up due to that!