Currently reading:
Phase to Earth fault on a 3 phase motor supply

Discuss Phase to Earth fault on a 3 phase motor supply in the UK Electrical Forum area at ElectriciansForums.net

What did you check the voltage with? A high impedance multimeter, or a 2-3mA voltage tester?

One phase welded shut so energising all 3 at the same voltage via the motor windings?

My first priority would be to verify the MCB is isolating all 3 phases, or when open check with voltage tester (carefully, this is live and dangerous) between the L1-3 supplies and the L1-3 out to see if you get 0V (contacts presumably welded shut) or ~230V (leak to earth) or 400V (one other phase not open).

Then check if there are any auxiliary supplies for control, etc, that might have faulted and are energising it.
 
What did you check the voltage with? A high impedance multimeter, or a 2-3mA voltage tester?

One phase welded shut so energising all 3 at the same voltage via the motor windings?

My first priority would be to verify the MCB is isolating all 3 phases, or when open check with voltage tester (carefully, this is live and dangerous) between the L1-3 supplies and the L1-3 out to see if you get 0V (contacts presumably welded shut) or ~230V (leak to earth) or 400V (one other phase not open).

Then check if there are any auxiliary supplies for control, etc, that might have faulted and are energising it.
I just tested with my Fluke Tester, not a multimeter. It was the same reading when the breaker was on, have not disconnected and taken out and changed the breaker yet.
 
What was the reason for being at the motor initially and testing?
I am doing some work at a block of flats, and was told the air extract was not working in the bathrooms. I checked the fan on the roof and it was not working. With the breaker on I was getting nothing between phases and 230 volts from each phase to earth, this was the same with the breaker off. I just used my Fluke tester, not a multimeter.
 
You need to do some systematic testing and work through the circuit. First check the output from the breaker and move on from there I would have thought there is some kind of overload relay at some point and if this has tripped you need to know why.
 

Reply to Phase to Earth fault on a 3 phase motor supply in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock