Currently reading:
Quick question and little help

Discuss Quick question and little help in the UK Electrical Forum area at ElectriciansForums.net

R

Ruso

Q-state 3 factors that influence selection of a protective device??

Would this be
1-cable size
2-ambient temp
3-equipment??

What you think? I've tried to answer best I can
 
2) Type of MCB/Fuse/RCBO is dependent of inrush currents. Simple example would be say a welding machine, because there are high currents (inrush currents) when the unit starts you would pick a D type breaker so that it would not trip, these loads are inductive loads. A immersion heater would only require a B type breaker as you would have none of these inrush currents and is call a resistive load. So you choice breaker will be dependent on type of load inductive or resistive

3) Depending on additional protection provided by an RCd. For instance circuits in a room containing a bath and shower have to be protected by 30mA RCD, so that influences your selection of protection devices, as it's a regulation, these regulations come under the Automatic Disconnection of Supply or ADS
 
Prospective fault current is another. Your chosen device must be capable of withstanding the higher of the prospective earth fault current, or prospective short circuit current of installation, if it doesn't then it could fail to operate in the required time, or not operate at all.

Cheers.........Howard
 
Q-state 3 factors that influence selection of a protective device?

I would say:-

1. The cable size and type of circuit. (6A, 10A,16A,20A etc)
2. Start up current. Type B, type C etc.
3. The maximum fault current it can handle without being replaced. eg 6KA, 10KA.


Ask yourselves this.... What three things are printed on an MCB?
 
the circuit breaker is chosen to provide safety for the circuit so,
(1) Cable size and test results so that it trips / blows before your circuit is damaged.
(2) Type of load so that you can choose B,C,D or RCBO or any other variant but for old fashioned rewire-able or cartridge then that would not be a factor.
(3) Type of enclosure no point trying to jam an MCB in to a rewire-able board or a new Wylex MCB in to an old Wylex MCB board as it just wont fit.
 
and a most important factor in selecting the correct protective device is..... can you get it in with a hammer...oops, sorry, thought i was on the plumbers forum. :drool5:
 

Reply to Quick question and little help in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock