Search the forum,

Discuss Rcbo in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

DaveyD

-
Arms
Reaction score
185
Hi everyone.
Im an electrician but I don't install PV

I am doing some works and changing a cu.


The customer already has pv fitted. There is no room to add a separate board and they have put a 16a mcb on the rcd side if the 16th edition board. TNC-S earthing arrangement. The cable is buried in the wall so it will need 30mA rcd protection.
They made a mess actually. Took the 16a mcb from the immersion heater circuit and put that 2.5 t&e in with the cooker on that 32a mcb and also nothing was re labeled on the cu.
Anyway. I've read that you should not share an rcd with pv because under fault on another circuit the rcd will trip and yet the back feed from the pv will keep the busbar live for up to 5seconds while it shuts down.
I've also read that you can't use a seperate RCBO even if its on its own bar as they down like to be back fed.
I'm assuming that it will work on a standard Ac rcd as it was working on the old one its on.


So without adding a separate board is there any way I can get this all on a split load board?
Tia
 
what's the inverter?

sma, power-one will usually be ok to back feed a standard Type A RCBO, others may inject too much DC current and need a Type B to cope with higher levels of DC injection.

But I'm not sure how you intend to fit this to a standard split load board, as don't they usually only have 2 neutral bars, so you'd be unbalancing the neutral going through the RCD. We'd usually use a high integrity board for this, but maybe you can adapt the board somehow to turn it into an effective high integrity board... ie with the PV not sharing a neutral bar with the RCD circuits.
 
what's the inverter?

sma, power-one will usually be ok to back feed a standard Type A RCBO, others may inject too much DC current and need a Type B to cope with higher levels of DC injection.

But I'm not sure how you intend to fit this to a standard split load board, as don't they usually only have 2 neutral bars, so you'd be unbalancing the neutral going through the RCD. We'd usually use a high integrity board for this, but maybe you can adapt the board somehow to turn it into an effective high integrity board... ie with the PV not sharing a neutral bar with the RCD circuits.
Thanks Gavin. Yes sorry it is a high integrity board. So a single rcbo can handle if the inverter is ok? I will check that tomorrow
 
Would recommend you fit an all-pole RCBO if you do go down that road. A single small inverter, depending on type "might" be ok on a 30mA RCD but be wary of nuisance tripping (if transformerless) and/or trip-coil saturation, dependant on the type of residual current detection fitted (Type-A dual-pole RCBOs are available)
 

Reply to Rcbo in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock