Discuss What are the regulations for PV consumer unit protection? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Az8124

DIY
Reaction score
0
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer unit protection required. I'm hoping someone may be able to clarify the protection required by the regulations in place last October.

I have a Solis S6 3.6kW inverter connected to our consumer unit. Initially this was protected by a 16A type B RCBO (Hager ADA316G) running into a double pole isolator and surge protection. The sparky at the time warned us one of these would need to be replaced in future however this was all he had available on the day. He also said he had had no formal PV training. Oddly, the documentation provided to us stated that the “PV system is connected to a dedicated 16A type B MCB in the consumer unit”.

After this I sought some advice from a trusted sparky and was told that we should have had an MCB installed but that this was only “advice” and not regulation because the company is not going back to fix any of their previous installs. So, I had this corrected and the 16A RCBO replaced with a 16A Type B MCB. Work which of course they want to charge for (while also removing the RCBO which I had already bought as well).

My concern is the conflicting “advice” and the fact that the company is happy to fit both breakers and charge for both. Could someone please clarify what should have been installed as consumer unit protection according to the regulations?
 
If the cable between the supply and the inverter is regular household twin and earth, and buried less than 50mm below the surface, or on the surface, then a 30mA RCBO would be right... just for protecting the cable. Do you know what size the cable is?

A 16A is cutting it fine if the invertor is generating the full 3.6kW.... most i've seen are oversized at 32A, with a 4mm cable to invertor.
Just to say, i am not a PV installer, but do take note when i see PV in houses ive been in.
 
There is no requirement to install RCD protection to PV system AC cable unless it's required because of installation method as mentioned above, or manufacturer instruction insist on installing one.
Looking at MI your system should be protected by 20A OCPD
 

Reply to What are the regulations for PV consumer unit protection? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Ok, installing a new CU with type 2 SP. The installation has an existing PV 6 panels protected by a 16a MCB at the fuse board. TBH I don't really...
Replies
0
Views
635
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
743
Had a customer ask for RCD to be changed to Type A as he has had a company install a PV unit which they have left with the spur switched off as...
Replies
13
Views
2K
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
886
Hello all, I'm in the process of having my kitchen refurbished and I'm looking for advice on my current setup as I have been told that I will...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock