Discuss RCD Test Failing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Have you tried testing with the circuit conductors disconnected from the RCBO?RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.
Am I missing something obvious? Thanks
Yes, it still fails the test with conductors removed. In fact, the issue is with 2 RCBOs on the same board now. Seems odd as they are brand new.Have you tried testing with the circuit conductors disconnected from the RCBO?
Hager Type AWhat make and type of RCBO? A/AC/B???
Thanks for that. The link seems to indicate RCCBs prior to July 2019?Hager recommend testing at the device not at the end of the circuit see this link https://hager.com/uk/support/regulations-18th-edition/updated-rccb-testing
Thanks for that. The link seems to indicate RCCBs prior to July 2019?
I’ve tested at 250ma and 300ma. Still having the same issue. The RCBOs pass the test when MFT is set to AC.are you testing at more than 250 ma we have had hagar rcd’s that don’t meet the required 40ms at 150
Bizarrely, BS7671 seems to be telling us to do exactly this:So when a product is faulty we alter the test parameters to ensure it passes?
not sure on the legalities of this.
the excuse is manufacturers instructions say to do this.
what takes priority b.s.7671 or manufacturers instructions?
if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.
very naughty!
It baffles me too. It seems that so long as it trips at any current => 150mA, all's well, but no need for it to trip at all at 30mA?
The product is not faulty, it is in line with the standards required for rcd/rcbos.So when a product is faulty we alter the test parameters to ensure it passes?
not sure on the legalities of this.
the excuse is manufacturers instructions say to do this.
what takes priority b.s.7671 or manufacturers instructions?
if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.
very naughty!
Agree. I was one of those that was unfamiliar with this reg. or the wording of reg until @Pretty Mouth pointed it out.The product is not faulty, it is in line with the standards required for rcd/rcbos.
It's just people are not familiar with it, there is no absolute requirement for 150mA or 5x , the requirement is the figure as published by the manufacturer, it was just normally 5x but didn't have to be.
Reply to RCD Test Failing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net