Currently reading:
RCD Test Failing

Discuss RCD Test Failing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
0
RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.

Am I missing something obvious? Thanks
 
Is there something in the installation that may be injecting dc into the supply?
 
RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.

Am I missing something obvious? Thanks
Have you tried testing with the circuit conductors disconnected from the RCBO?
 
What make and type of RCBO? A/AC/B???
 
Replaced the RCBOs with new ones and still having the same problem. Tried it at the socket (outdoor), and at the DB with the conductors disconnected. RCBO still failing for additional protection at 5X In (56ms).

Any ideas what could be causing this? Cheers
 
So when a product is faulty we alter the test parameters to ensure it passes?

not sure on the legalities of this.

the excuse is manufacturers instructions say to do this.

what takes priority b.s.7671 or manufacturers instructions?

if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.

very naughty!
 
So when a product is faulty we alter the test parameters to ensure it passes?

not sure on the legalities of this.

the excuse is manufacturers instructions say to do this.

what takes priority b.s.7671 or manufacturers instructions?

if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.

very naughty!
Bizarrely, BS7671 seems to be telling us to do exactly this:

643.8
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1 disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating current.

That's 'or', not 'and'. Poorly written reg, or deliberate?
 
I believe Hager have addressed this but the Regulation quoted in #16 takes into the requirements of EN61008 which allows for ×5 and above.
 
Last edited:
The issue isn't BS7671 nor the manufacturer's instructions, it's actually in bsen61008 and 61009 - the standards for the devices themselves, basically it has to operate above the set current (say 30mA), but does not have to do so within 40ms.

In addition, it must operate at 5x - OR at a figure declared by the manufacturer within 40ms.

BS7671 reflects this info poorly however.

So you must test to ensure an rcd or rcbo trips at its setting (typically 30mA), and in addition operates within 40ms at the figure declared by the manufacturer (typically 5x setting).

If it trips at 30mA within 40ms, actually there is no need to do a 5x - it's already passed!

Unfortunately those manufacturers who chose a different value than 5x as the trip time test current are finding loads of people claiming failures because they automatically test at 5x, of course the rcd is compliant (assuming it does trip in time at the correct test current), so it's becoming easier to change the product rather than deal with all the "false failures"

Normally instead of 150mA (5x) most chose 200mA as their test current for trip time.

I have a megger mft1731 which only does 5x so if I have to test a rcd/rcbo which has this 200mA value, I use the 30mA setting for trip operation, then the 40mA (operator set) setting at 5x for the trip time (unless it happens to pass at 150mA)

Hagar are 250mA.
 
So when a product is faulty we alter the test parameters to ensure it passes?

not sure on the legalities of this.

the excuse is manufacturers instructions say to do this.

what takes priority b.s.7671 or manufacturers instructions?

if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.

very naughty!
The product is not faulty, it is in line with the standards required for rcd/rcbos.

It's just people are not familiar with it, there is no absolute requirement for 150mA or 5x , the requirement is the figure as published by the manufacturer, it was just normally 5x but didn't have to be.
 
The product is not faulty, it is in line with the standards required for rcd/rcbos.

It's just people are not familiar with it, there is no absolute requirement for 150mA or 5x , the requirement is the figure as published by the manufacturer, it was just normally 5x but didn't have to be.
Agree. I was one of those that was unfamiliar with this reg. or the wording of reg until @Pretty Mouth pointed it out.

also as @Pretty Mouth says I’m a bit baffled by it.
 

Reply to RCD Test Failing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock