dlt27
-
- Reaction score
- 26
Had quite a few problems lately with rcd's on dual boards tripping and on 2 occasions I haven't been able to find the problem (trips once every couple of days) . I have meggered circuits, ramp tested rcd, used megger mA meter for earth leakage etc. On both occasions there was an earth leakage of 10mA for entire board so shouldn't trip rcd. However I changed rcd to rcbo's and haven't had a call back since.
I have heard in the past people saying about external influences causing rcd's to trip. However I don't understand how this works. Can somebody explain in simple thick electricians terms how this can happen. The funny thing is with the last rcd the owner said it only started tripping since eon replaced an 11KV overhead cable.(Last one was taken down live by tatters). Thanks to anyone who has patience to explain....
I have heard in the past people saying about external influences causing rcd's to trip. However I don't understand how this works. Can somebody explain in simple thick electricians terms how this can happen. The funny thing is with the last rcd the owner said it only started tripping since eon replaced an 11KV overhead cable.(Last one was taken down live by tatters). Thanks to anyone who has patience to explain....