UK RCD Tripping

Discuss RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Evening, came across a fault today on a new board that’s been fitted by a previous electrician. Split load dual RCD 6 way Hager board, when a fused spur is switched on or when the boiler starts up the RCD trips but the circuit is on the other RCD. Have checked the all wiring at the DB and all is ok. The previous board was a old wylex 100ma RCD board and never tripped.
 
Borrowed neutral was my thinking. However the previous electrician fitted a single 30ma RCD board before this board and it still tripped. Earth leakage is too high for a 30ma RCD, but why would the other rcd trip and not the rcd protecting the circuit?
 
Evening, came across a fault today on a new board that’s been fitted by a previous electrician. Split load dual RCD 6 way Hager board, when a fused spur is switched on or when the boiler starts up the RCD trips but the circuit is on the other RCD. Have checked the all wiring at the DB and all is ok. The previous board was a old wylex 100ma RCD board and never tripped.
I had a similar problem couple of years ago. RCD2 was tripping whenever any load was put on kitchen ring baffled me. I carried out insulation resistance test and found that the fault was on the downstairs lights which was on RCD1 screw touching neutral in living room light. It was also a Hager split load board. Do an IR test on circuits that will find the fault for you.
 
Had a fault similar to this about a year ago and the fault was on one of the circuits off the RCD that was tripping, had me puzzled for a while especially when I did an RCD test on the incoming side of the RCD's and it tripped the RCD, fault was found using a cable locator to be a floorboard nail partially through a cable
 
N-E fault could be on one of the circuits that is on the RCD side that is not tripping. take the suspect N's out of bar and IR test.
 
last 1 i had was shower switch N-E fault. switch on kettle (on the other RCD) and it tripped.
 
So yesterday the owner disconnected a lighting circuit from the side that tripped and everything worked fine, didn’t trip once.
my tester is being calibrated at present once it’s back I will carry out the tests.
 
So there are 3 lighting circuits, one for the landing and 2 bedrooms, bathroom and the 3rd bedroom. He disconnected the 3rd bedroom as a elimination process. He’s very adamant to fix this himself.
One of those customers that wants your help but wants to do it all himself
 
So there are 3 lighting circuits, one for the landing and 2 bedrooms, bathroom and the 3rd bedroom. He disconnected the 3rd bedroom as a elimination process. He’s very adamant to fix this himself.
One of those customers that wants your help but wants to do it all himself
Let him fix it then, but if he calls you back, charge him extra for putting right what he's maybe mixed up.
ie neutrals and cpc not in the same numbers as the lives.
 
So there are 3 lighting circuits, one for the landing and 2 bedrooms, bathroom and the 3rd bedroom. He disconnected the 3rd bedroom as a elimination process. He’s very adamant to fix this himself.
One of those customers that wants your help but wants to do it all himself
Sounds like my sister's father in-law, he got a roofing contractor to sort his roof out, but ended up on the roof doing it, and the contractor passing up the roof tile's lol
 

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock