Was at a property toady which I've done previous work before including fuseboard change. All i did today was change a few socket plates over for new ones. Took some Zs readings and noticed they were very near the limit of being acceptable ie: 0.92, 0.98 etc.
Took a Ze at the board with main earth disconnected 0.06
reconnected and took various 3 wire no trip loop tests at different positions in DB. basically i was getting nice low readings on the supply sides of rcds but on the load side of both of them i was getting about 50ohms higher.
The RCDS are MK and only fitted about 6 months ago and when originally fitted tested out fine.
I also ran through standard RCD tests to see if they were ok which they were. ZS results were still high after this too.
Also checked busbar and neutral leads were properly connected in the load side of rcds, which they were.
Never have this happened before, didnt know if anyone else had. Do you think RCD replacement could be required?
cheers
Took a Ze at the board with main earth disconnected 0.06
reconnected and took various 3 wire no trip loop tests at different positions in DB. basically i was getting nice low readings on the supply sides of rcds but on the load side of both of them i was getting about 50ohms higher.
The RCDS are MK and only fitted about 6 months ago and when originally fitted tested out fine.
I also ran through standard RCD tests to see if they were ok which they were. ZS results were still high after this too.
Also checked busbar and neutral leads were properly connected in the load side of rcds, which they were.
Never have this happened before, didnt know if anyone else had. Do you think RCD replacement could be required?
cheers