I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on it which double up as junctions. I find that hard to believe.
 
Last edited:
A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.

Spurs do not have to be taken from sockets, they can be taken from a suitable joint box or from the origin of the circuit.


As always the above refers to the 'standard circuits' as described in the regulations and supporting publications. If you wish to design your own non-standard circuits then you are free to do so, however you would need to fully document the design (as a courtesy to anyone else who has to work on the installation, as defense should anything go wrong, as defense when an EICR is carried out and the non-standard design is flagged up, etc etc)
 
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.

No, it can't, not as a standard ring final circuit.

As I said, a ring can only have as many unfused spurs as it has sockets connected to the ring.

On your ring of cable with joint boxes, if you intend it to be a standard ring final circuit, you cannot have any spurs as you have no sockets on the ring.
 
What would lead you to design a circuit like this?

If you can get one cable to a socket, then you can get two.
It has no financial benefit, as the cable saving is countered by joint boxes and time making those extra joints.
The extra joints also add another point of possible faults.

In technical terms…. This is how a standard socket is. The joint is the terminals on the back of the socket… the “spur” is the internal metalwork between the terminal and the contacts for the plug pins.
 
Perhaps there is more to JSJW's design than he is letting on, but per post #6 what would be the point? Just as easy to accommodate sockets into the RFC!
 
Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.

As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.


Get your replies in now, lads…. Can’t see this thread lasting much longer. 😆
 
Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.

As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
 
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
What about the cost of the joint boxes or are you not going to answer that.
There are plenty of ring final circuits out there which do not incorporate socket outlets.
 

Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock