Search the forum,

Discuss sharing one MCCB for 2 loads in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Happy new year everyone!
During one my my inspections in an existing warehouse, I saw their electrician has pulled a wire from the incomer side of an existing panel ( panel A, 3 pole isolator as an incomer), to feed another e phase panel(panel B). The upstream breaker is an MCCB ( in panel C) with sufficient rating for the total load on both panels.(pls see the attached image)
(on the upstream panel, there is proper marking that it is feeding 2 panels, the cable size is sufficient for total load,..etc)
what can go wrong?! I know it is not correct, but what are the risks in terms of safety?
 

Attachments

  • IMAG0017_1.jpg
    42.7 KB · Views: 37
Separation of circuits requirement? Bit inconvenient where you needed to isolate only one DB from source. I would rather (personally) have taken the extra supply from a 3pole MCB in the board for isolation purposes. Granted it may not have had room.
 
Separation of circuits requirement? Bit inconvenient where you needed to isolate only one DB from source. I would rather (personally) have taken the extra supply from a 3pole MCB in the board for isolation purposes. Granted it may not have had room.

However that will probably create a discrimination issue.
Each board can still be isolated via its main switch.
Two DBs fed from the same submain is no different to one DB twice the size fed from the submain.
 
Separation of circuits requirement? Bit inconvenient where you needed to isolate only one DB from source. I would rather (personally) have taken the extra supply from a 3pole MCB in the board for isolation purposes. Granted it may not have had room.
True. Isolation of each DB from source was what I was thinking as well.
 

Reply to sharing one MCCB for 2 loads in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top