Discuss The EC Fan keeps tripping the RCD in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
4
Hi All,

Weird matter happening here and I hope you can help!

My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature setpoint. A control panel to manage the EC Fan is in the room. EC Fan above faux ceiling. The panel has it's own MCB. The RCD is upstream, before the maintenance isolator upstream the panel.
So, inside the panel: MCB.
Outside the panel upstream: isolator.
upstream the isolator, in a separate room: RCD.

Everytime I switch off the isolator to the panel, the upstream RCD (from the other room to the panel) trips.

Based on the EC Fan contractor, I must increase my RCD sensitivity from 100mA to 300mA to solve the issue. Also, it seems the problem is the panel.

Based on Panel contractor, the panel is fine. The problem is the EC Fan.

As a matter of fact, after an initial investigation, it seems that when I open my isolator, there is a "weird" returning path to neutral. What I mean is: I open the isolator, measure between L1 upstream the isolator and the Neutral downstream the open isolator and fine 240V. I thought it was merely induced. But when a load is connected to those wires, the lights is ON. Clearly it's a ligit path.

Based on my electrician, that returning path to Neutral should not exist, even with an EC Fan. How comes that my EC Fan comes with a Neutral wire that is solidly connected to ground? Why my.RCD trips only when switched OFF and not during operation as well?

Thank you in advance All.
Mark
 
i think that is fault in isolator.
when isolator is opened, it seems that phase line and grounded neutral line are in contact.
so, i think RCD was triped beacuse detected leakege current.
 
i think that is fault in isolator.
when isolator is opened, it seems that phase line and grounded neutral line are in contact.
so, i think RCD was triped beacuse detected leakege current.
Thanks for your reply and good guess. I tried that by totally disconnecting the cables from the isolator. The weirdest thing is that I still measure 240V between upstream the isolator and the totally disconnected neutral from downstream. Not sure why
 

Reply to The EC Fan keeps tripping the RCD in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
319
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
740
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock