I had the house rewired about 18 years ago the electrician used 1 mm twin and earth from a 6 amp breaker in the consumer unit to a fused spur with 3 amp fuse for the combi boiler, I am about to have a new boiler installed and want to know if this cable is actually the correct size it has caused no problem but I would have thought 1.5 was more suitable.
 
The current Regulations now prohibit the use of 1mm² cables for power.
The minimum CSA is now 1.5mm².
However that not withstanding, 1mm² should be more than adequate for your combi boiler, especially if the rating of the fuse is still at 3A.
 
I had the house rewired about 18 years ago the electrician used 1 mm twin and earth from a 6 amp breaker in the consumer unit to a fused spur with 3 amp fuse for the combi boiler, I am about to have a new boiler installed and want to know if this cable is actually the correct size it has caused no problem but I would have thought 1.5 was more suitable.

Are you replacing a boiler or installing a large kettle? 1.0mm is more than sufficient to supply the new boiler!
 
I suppose you can interpret the Reg. however you wish.
How do you interpret the table to mean anything other than what it states?
Lighting 1mm².
Power1.5mm².
Is a combi, some new form of lighting, should I re-lable all the CUs from boiler to lighting?
 

Reply to Size or Cable for Combi Boiler in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The new Advance Combi Boiler has a feed from consumer unit using 6mm cable on a 32amp breaker to a 45amp double pole switch. What size cable to...
Replies
9
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
594
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock