Hi,
I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself.
Boiler: Ideal Logic Max 35KW Combi
I've researched the electric supply requirements from the manufacture (image below)
My consumer unit has a spare Contactum 7106B 6A breaker
I plan to run 1.5mm Twin & Earth from the above breaker to a 3A DP switched fused spur. The cable run is roughly 6 meters. Am I missing something or is it this straight forward?
Worth mentioning the Gas and Water pipes are bonded at the meters. After reading BS.7671 regs (below) I'm not clear on If I need to bond the pipes at the boiler too:
BS.7671: Domestic installations
• Take one bond to incoming metallic water and gas pipes.
• If there is a metallically piped central heating system, bond it in one location. This is not necessary where any metallic pipe, bonded elsewhere (e.g. metallic water pipe), is connected and tests satisfactorily for continuity.
• If the structure is metallic, take a bond to one location; this is not necessary for intermediate metallic stud partitions or individual metal beams and the like.
• The central heating system will probably not need a cable bond connection if connected by metallic gas or water pipes which have themselves been bonded
I will be getting an EICR test done but this is likely to be after I've run the new circuit.
Boiler manufacture:
Any help, comments or advice is much appreciated.
Thank You
I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself.
Boiler: Ideal Logic Max 35KW Combi
I've researched the electric supply requirements from the manufacture (image below)
My consumer unit has a spare Contactum 7106B 6A breaker
I plan to run 1.5mm Twin & Earth from the above breaker to a 3A DP switched fused spur. The cable run is roughly 6 meters. Am I missing something or is it this straight forward?
Worth mentioning the Gas and Water pipes are bonded at the meters. After reading BS.7671 regs (below) I'm not clear on If I need to bond the pipes at the boiler too:
BS.7671: Domestic installations
• Take one bond to incoming metallic water and gas pipes.
• If there is a metallically piped central heating system, bond it in one location. This is not necessary where any metallic pipe, bonded elsewhere (e.g. metallic water pipe), is connected and tests satisfactorily for continuity.
• If the structure is metallic, take a bond to one location; this is not necessary for intermediate metallic stud partitions or individual metal beams and the like.
• The central heating system will probably not need a cable bond connection if connected by metallic gas or water pipes which have themselves been bonded
I will be getting an EICR test done but this is likely to be after I've run the new circuit.
Boiler manufacture:
Any help, comments or advice is much appreciated.
Thank You
Last edited: