that would be fine if your also using a contactor and overload relay that is set to FLC of motor.

but if that is the only device protecting the motor from overload then as @SheffSimon says above, get the correct matched rating (nameplate of motor, not actual current measured) or the motor will burn out before the breaker trips.
 