Discuss Star/delta starter to dol 4kw in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi

Changing a 3 phase star delta motor and replacing with a dol 3 phase motor.

Would i be right in thinking I can remove 3 of the 6 cables at the isolator and make sure I use the ones coming off the delta contactor to get the motor up and running for now.
 
No the motor will need connecting for delta at the motor terminal box and you would need to ensure correct rotation.
 
have you a picture of the motor nameplate?
 
Why are you doing this, you potentially could cause mains transients on smaller power networks and local installations, the reason it has a star/delta starter on is to suppress inrush currents when energising motors, it is recommended to have some form of soft starting method for motors 4kw and above.
To note here if your actions do cause power network/grid transients you and/or the company could face fines so I would take this into account, again, is there a valid reason to do this?
 

Reply to Star/delta starter to dol 4kw in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I want to benefit from your experience regarding a delta secondary service. We are upgrading an electrical vault. On the primary side, we are...
Replies
0
Views
297
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
455
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock