Search the forum,

Discuss Strange/Unusual Fault in the UK Electrical Forum area at ElectriciansForums.net

Then if it's that strange carry out two seoerate tests , the wiring and the power consuming equipment \, to try and eliminate one from the other, no good just testing it all in one procedure, any good detective will tell you to eliminate one area at a time just saying, others may call me an idiot, but been called worse. and have a thick skin.

Yes obviously 2 separate procedures ?

I wouldn't combine them

Test the cable at a high voltage and equipment separately , I didn't imply differently
 
He did say clearly in post #1 that the loads were tested separately and the problem was still there with them disconnected.

Presumably the socket was included in the IR tests that showed 70 / 140 megs? In which case it doesn't seem to be particularly suspect.
 
So there I was the other day posting on here about me going to solve faults others couldn't find and I've got one myself.

It's been a while since I've been stumped but I am now.

Symptoms - gate supply keeps tripping (when it's raining according to customer). There's a 6mm 3 core SWA running about 3-400m (yes you read that right), to a cabinet by the gates where there is a double socket inside feeding a right mess for the gates. Protected by Hager reduced height 20A RCBO.

Unplugged both sockets, IR tested cable from consumer unit to double socket.

L-N = 140Mohm
L-E = 71Mohm
N-E = 70Mohm

IR tested the plugs for the gate controls. L&N together to earth. One was 12Mohm, the other was 299Mohm. Throughout all the below I never plugged the gates back into the double socket.

With the plugs still unplugged and nothing in the double socked I went to turn on the RCBO. Took 4 goes to get it to stay in. No bang, just as if there was N/E fault there. 1/2 trip and ramp tested RCBO and both returned no result as it tripped so early/quickly. Removed outgoing cables from RCBO and all tested well - 23mA ramp test and turned on without any trouble.

Changed RCBO to rule that out and same symptoms.

Tested IR a few more times to make sure and same results. Tested outgoing cables to socket to all other cables in consumer unit to see if anything was mixed up. All good. Physically traced cables in consumer unit to check same and again all good.

I'm guessing it's something to do with the length of the cable? I can only guess that somehow I'm losing current from the line to the earth as they are run alongside eachother for such a distance? This doesn't really make sense to me though. Someone put me out of my misery!

Strange set-up, certainly no design to this circuit.

What is the design current for the gates?

You would need a B10 60898 upstream to meet disconnection times.

As it's SWA can you swap out the upstream RCBO to an MCB and fit RCD socket at the gate for the additional protection?

Certainly would not have been a cheap install for 3-400m of 3C 6 XLPE!
 

Attachments

  • SLD.PNG
    23.1 KB · Views: 38
  • Cable Calc.PNG
    196.9 KB · Views: 38
No idea re gates design current. No details present. To be honest I’m trying to stay well away from that side of things. It’s a single ram type arm that opens 1 gate.

Doubt that total load can be much. A B6 mcb would comply and might work fine? I guess the motor should only be a few hundred watts. Anyone like to make a guess?

I forgot I have a picture of the completely typical gate wiring I find whenever I look inside one of these cabinets. Utter disgrace in there.
 

Attachments

  • 76890B72-8775-466E-BEFB-978151F5A8C5.jpeg
    750.4 KB · Views: 39
No idea re gates design current. No details present. To be honest I’m trying to stay well away from that side of things. It’s a single ram type arm that opens 1 gate.

Doubt that total load can be much. A B6 mcb would comply and might work fine? I guess the motor should only be a few hundred watts. Anyone like to make a guess?

I forgot I have a picture of the completely typical gate wiring I find whenever I look inside one of these cabinets. Utter disgrace in there.
There wouldn't be much load on the bowl of spaghetti!

You could always try squeeze in an IP rated RCD socket lol!
 
I think my approach would be to try and get an accurate Zs, as the length is a bit of an unknown making any attempt to introduce design into this a bit hit and miss. Current bets are it being longer than 400m based on your 4 ohm non-trip Zs.
So either dead tests, or stick any low-ish breaker in and a high current test, hence working out max breaker size up top. Fitting an RCD enclosure inside the gate box could be be the fun part.
It could always be an IP enclosure on the outside. In fact I might prefer the customer not to have to open that can of worms to reset it!
 

Reply to Strange/Unusual Fault in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock