Discuss Sub mains for extended distance from meter to CU in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
As the user name states, I am not an electrician but I am trying to be an informed customer when dealing with a friendly local sparky and the DNO/supplier whilst undertaking some major electrical works on my property and some advise on the best solution would be welcome.

The works to be undertaken:
  • Move of meter from high level on an interior wall to a low level external surface mount box on the other side of the same wall
  • Move and replace the fuse wire fuse box with a metal clad CU
  • Improve the earthing situation of the property
  • Complete rewire creation of new ring mains & lighting circuits to provide seperate circuits for differnt parts of the house.
The situation:
  • The house is a 1950s bungalow with solid block walls
  • Supply is a TT system from overhead cables that are clipped to the side of the house and the soffits before enter the loft breify and dropping down the the 100A DNO fuse and the meter.
  • Current earthing arrangement is completely inadequate with 1x 1.5mm cable on the water pipe before it changes into plastic to the street and 1x 1.5mm to an earth stake in the front garden.
  • The preferable location for a new CU is in a cupboard approx 6m of cable run from the proposed meter location and would require running in the loft above insulation that is yet to be fitted.
Suggestion I am hoping to put to SSE and local contractors include:
  • Changing the earthing arrangement from TT to a from of PME if availble
  • Installing a fused switch at a location close to the new meter to keep the new 25mm meter tails <3m and a new cable run from there to a CU.
Options I am considering for the meter to CU connections that I would like advise on please:
  1. Short meter tails to an externally mounted box containing a fused switch or large double pole RCD and then run either SWA up the outside of the house into the loft and down to the CU or come out of the back of the box into a void behind a false wall and up into the loft that way.
  2. As above in SWA tails to a fused switch located in the loft and then in SWA or other more flexible cable if mechanical protection is not required to the CU
  3. Mount an RCD in the meter box and run the cables out the back of it into the false wall void and up into the loft.
This void is being created to hide dental heating pipes located on the opposite side of the door frame to the proposed electrical runs and would create a space approx 50-60mm deep and 70mm wide in a safe zone next to the front door.

Taking people's better understanding of the regs into cinsideration and the bend radius of the swa that I am expecting to need to use at some point in this (I use it a lot at work and know it can be a pig)

A) are any of these suggestions valid
B) which would people recommend I suggest to a qualified electrician.

Thanks
 
The first part, changing the supply, you will need to enquire with your DNO to see if there's scope to change, and how much it will cost.

I would approach that aspect first before proceeding further.
 
The first part, changing the supply, you will need to enquire with your DNO to see if there's scope to change, and how much it will cost.

I would approach that aspect first before proceeding further.
Thanks, I have done so this week and raised a change of supply request with SSE, they are due to be in touch next week, I asked them about the PME and the relocation of the meter and all seemed ok. they could not stipulate the length of the meter tails over the phone but did say they will need to be 25mm.

What do you think about the options for getting from their fuse to a new CU?
 
Thanks, I have done so this week and raised a change of supply request with SSE, they are due to be in touch next week, I asked them about the PME and the relocation of the meter and all seemed ok. they could not stipulate the length of the meter tails over the phone but did say they will need to be 25mm.

What do you think about the options for getting from their fuse to a new CU?
By 25mm I think they mean 23mm2 the CSA of the tails. As you have already approached SSE regarding moving the supply and costings.
I think your next step should be to contact electricians in your area to give you a costing of the other works you are intending.
 
Thanks, I have done so this week and raised a change of supply request with SSE, they are due to be in touch next week, I asked them about the PME and the relocation of the meter and all seemed ok. they could not stipulate the length of the meter tails over the phone but did say they will need to be 25mm.

What do you think about the options for getting from their fuse to a new CU?
Have you enquired about moving the supply near to the location where you want the new consumer unit.

That would be my first option.
 
Have not spoken to the distributor about moving the supply that far and am unsure if that would be possible.

The thought process for moving it to the outside wall close to where the meter is now is that I believe there is a difference between moving it over and under 1m from its current location and to move it closer to the preferred CU location would mean running the overhead supply into the loft for 3-4m before coming down into a cupboard with no outside walls and locating the meter in there.

Besides the additional space required is that a feasible option when planning the layout of the new system? I have in my head that the supply should terminate at the entrance to the property?
 
Have not spoken to the distributor about moving the supply that far and am unsure if that would be possible.

The thought process for moving it to the outside wall close to where the meter is now is that I believe there is a difference between moving it over and under 1m from its current location and to move it closer to the preferred CU location would mean running the overhead supply into the loft for 3-4m

I subbied on a job, where the DNO (SSE) did just that. You'll have to see what they say.
 
I would want to get the SSE cables off my house. Would it be possible to run a cable from the nearest pole? If it is in or adjacent to your garden you could do the excavation which would considerable reduce the cost. The meter box could then be placed back to back with the CU, drill through the wall and the tails will be less than 3m so no switch fuse required.
 
The pole is in my back garden and my and my attached neighbours supplies are fixed to my house, at some point the previous owners of next door have moved their meter to the outside wall like my original thoughts but I believe they had kept the consumer unit in the kitchen back to back with the meter box. layout changes in my property mean this is a less feasible option.

I had not considered changing the cabling to an underground setup but I would still have the issue with locating a meter in the centre of the house or a longer run to the CU.

Thanks for all the responses people, This is giving me a lot to think about. It's only these 2 houses on the street that have an overhead supply, all the newer properties have an mordern underground (TN-C-S?) supply. I had previously dismissed contacting the DNO regarding the possibility of connecting to this system instead - should I put that back on the table in discussions with them next week?

I am intrigued by the possibility of the supply terminating in the centre of the property, This is a potential solution that I did not think was an option. Time will tell if SSE will allow me to request this.
 
I am intrigued by the possibility of the supply terminating in the centre of the property, This is a potential solution that I did not think was an option. Time will tell if SSE will allow me to request this.

The only thing to be aware of, is their supply cable has no steel armouring like swa cable. Careful consideration needs to be taken on them routing their cable. Loft insulation, and mechanical damage from suitcase, Scalextric sets & Xmas decorations could be an issue :)
 
Most DNOs have rules that say service cables in customers houses should be protected by a 100A fuse in in a fireproof pipe, but we have all seen loads of cases where this is not the case.
 
SSE have been out, had a look and given me a quote to alter the supply.

There are a few details in the quote I need to discuss with my builders electrician but extending the supply into the property does not appear to be an option. They are stipulating 25mm tails of no more than 3m.

After reading what SSE have to say the currenty preferred solution would be for an externally mounted meter with 3m SWA tails to a 100A fused switch in the loft and then a further 5m run of 25mm swa clipped direct to a CU located in cupboard in the habitable space of the house.

Do you professionals out there fore see any issues with this as a plan for me to put forward to my builder who will be installing the meter box and his electrician who will be doing the works?

I am suggesting the tails are clipped to the external masionary (on a shaded side of the house) before entering the loft space.

As for temperature de-rating of the cables in a "cold roof" loft - all insulation is now currently below the cable runs for the existing wiring and shall remain that way for the house re-wire for the time being. Would that mean:

30degC ambient current carrying capacity, referance C for clipped direct = 146A?

An estimated maximum ambeint loft temperature = 50degC due to lack of insulation and therefore Ca = 0.82?

Would this still give a current rating of 119A for the cable after the 100A fused switch?

The loft is border with lights and a fixed ladder for access as this is where the boiler is located. I am not proposing that I suggest to the electrician the CU is located up there only the fused switch for the sub main, the operation of which should very rarely if ever be needed.

Are there any regulations which state this could not be done this way?
 
SSE have been out, had a look and given me a quote to alter the supply.

There are a few details in the quote I need to discuss with my builders electrician but extending the supply into the property does not appear to be an option. They are stipulating 25mm tails of no more than 3m.

After reading what SSE have to say the currenty preferred solution would be for an externally mounted meter with 3m SWA tails to a 100A fused switch in the loft and then a further 5m run of 25mm swa clipped direct to a CU located in cupboard in the habitable space of the house.

Do you professionals out there fore see any issues with this as a plan for me to put forward to my builder who will be installing the meter box and his electrician who will be doing the works?

I am suggesting the tails are clipped to the external masionary (on a shaded side of the house) before entering the loft space.

As for temperature de-rating of the cables in a "cold roof" loft - all insulation is now currently below the cable runs for the existing wiring and shall remain that way for the house re-wire for the time being. Would that mean:

30degC ambient current carrying capacity, referance C for clipped direct = 146A?

An estimated maximum ambeint loft temperature = 50degC due to lack of insulation and therefore Ca = 0.82?

Would this still give a current rating of 119A for the cable after the 100A fused switch?

The loft is border with lights and a fixed ladder for access as this is where the boiler is located. I am not proposing that I suggest to the electrician the CU is located up there only the fused switch for the sub main, the operation of which should very rarely if ever be needed.

Are there any regulations which state this could not be done this way?
I think SSE mean that the Tails should be no more than 3 Mtrs from their service head to the connections to the CU
 
You can locate the switch-fuse where you wish provided it has suitable access and does not exceed 3m from the service head. Best person to ask is your builders electrician.
 
I personally do not like the idea of a switch fuse isolator in the loft, although have seen it before!
I would recommend an externally mounted IP rated enclosure (or another meter box) adjacent to the meter box housing the S/Fused Isolator and run the swa from there. Meter tails will be less than a meter in that case. Explore other routes for the swa!

As for calculating current carrying capacity, I would leave that to the professional electrician doing the work depending on installation method he/she suggests.
The DNO OCP device is likely to be rated at 100A irrespective of you calculating 119A, or the tabulated CCC of the cable.
 
currenty preferred solution would be for an externally mounted meter with 3m SWA tails to a 100A fused switch in the loft and then a further 5m run of 25mm swa clipped direct to a CU located in cupboard in the habitable space of the house.

25mm is big and awkward to work with in a domestic setting, and usually completely unnecessary.

Unless youve got an exceptionally high power demand a 63A supply to the CU will normally be more than enough.
 
Resurrecting an old thread now, but things have been on hold for a while.

Am keen to get the meter move sorted out and the full house rewire that follows done but before that can happen there are a couple of issues that I would welcome the forums advise on please, though first some history:

Just before lock down work was being done on my place whilst I was away for work myself. 2x new recessed meter boxes had been installed adjacent to each other in a location agreed with SSE, one for their meter and cut out and the other for a fused switch.

The builder who had kindly taken charge of organising everything whilst I was not around arranged for an electrician to:

  • Install the fused switch
  • Mount the new consumer unit in the new location (old hot water tank cupboard, I put a combi in so this is now an empty space)
  • Run SWA between the 2x locations and terminate ready for the meter to be moved.

Prior to leaving I put notices on the walls for the preferred location of the new CU and spoke with the builder about the preferred route of the SWA in the loft.

All appeared to have gone well until I returned home into lock down to find the new consumer unit had been installed in a different location to where I had asked and to do so they had taken out the plumbing to my shower to fit the CU in and the route in the loft was not what I was expecting either.

I had asked for the CU to be at high level on the left hand wall of the cupboard, just below the celling with a second option of at mid level on the same wall if there are any regulations say I cant have it up high?

Instead it was put at mid level on the back wall of the cupboard, making it hard to access over the machine machine that will be located in there and disbanding the shower plumbing. I had also asked for the SWA to be clipped to the purling or other way of keeping the cable off the ceiling rafters as only half the final roof insulation is currently in place to make the wiring and plumbing works easier. Instead it was neatly clipped to the celling rafters and would be sandwiched between the layers of insulation when the works are complete.

The first thing I had to do when returning home was disband much of what had been done and pull back the SWA so that I could plumb the shower and this is the currently state of play.

I am considering my options, either asking the sparky to come back and redo it or just redoing it myself and getting them to pick up from where they left off but with everything in a different location.

The 25mm SWA that was used is too short to be rerouted to the preferred location in the cupboard if it remains clipped to the celling rafters and would need to cross over several water pipes and over roof timbers that tie the rafters together and does not appear to be a sensible route to get it to where it needs to be, run higher up as per my preference it would be even shorter and is 3-4m shy.

A couple of questions here please:
  • Are there any regulations in the new book that stipulate the mounting locations of a CU which would prevent it from being mounted close to the celling?
  • Are there any issues with clipping SWA direct to purlings onto which T+E is already mounted for some lights and sockets?

I would very comfortably pull in and terminate 25mm SWA myself, in fact whilst this work was going on in my house I was in a factory in Scotland working with the same size cable for the VSD supply to the new motor I was installing and pulling back/re-terminating 95mm SWA for the associated control panel we were moving and re-wiring. I am an industrial burner engineer and the equipment we install often uses some chunky cable. (just to give some context picture of the burner in question is attached - there is more to go on top still from the scaffolding)

Which brings me on to my second set of questions, when looking at the works in the new meter boxes the SWA was not terminated on the outside of the box like I would have expected, I would have expected to see it glanded off on the outer box and run the inner sheath through a stuffing gland on the fused switch with a separate earth from the banjo to the casing of the fused switch.

Instead a large hole was knocked in the meter box entry location and the full cable was glanded off on the fused switch - this must have been a challenge given the bend radius of the cable and result in it being incorrectly terminated with the sheath showing.

The meter tails to the adjacent box are also a point of concern, additional holes had been knocked (none of these holes were made with a hole saw or a die punch but look to be a hammer and screwdriver affair) towards the rear of the box to enable the tails to be passed though the cavity wall between the boxes. I would have at least expected cut holes and rubber grommets to prevent the chafing of the outer insulation that is evident on the meter tails.

  • Would it be correct to gland off the SWA on the outer box?
  • Is it ok to run the meter tails though the cavity between the boxes and should it be glanded?

I am not really planning on doing too much of the works myself, nor am I after a stick to beat the professionals who have done the works so far but rather some advise on the best practices in this situation please so I can continue with the renovations.

And now for some pictures:

Random photo of my day job.
20200309_155052.jpg


Hole in rear of meter box and meter tail chafing.
20200321_135606.jpg


Location of new CU and the disconnected but open ended plumbing as found.
20200321_125533.jpg


2x new meter boxes.
20200606_163938.jpg


Tight bend radius and exposed SWA armour.
20200606_164015.jpg


Any comments the forum may have will be welcome, Thanks.
 

Reply to Sub mains for extended distance from meter to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
801
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
351
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.