Supply to garden room with hot tub

Discuss Supply to garden room with hot tub in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
There’s is currently a 3 core 6mm swa installed/40amp breaker, the garden room has its own consumer unit with a 32amp ring circuit and 6amp lighting.
The ring circuit has a 1kw heater and a computer/ printer so not a lot of load and the lights are led -total 60w.
They now want a 32amp hot tub supply.
do I need to install a new 3 core 10mm? Or would 3 core 6mm just be ok?
thanks
 

There’s is currently a 3 core 6mm swa installed/40amp breaker, the garden room has its own consumer unit with a 32amp ring circuit and 6amp lighting.
The ring circuit has a 1kw heater and a computer/ printer so not a lot of load and the lights are led -total 60w.
They now want a 32amp hot tub supply.
do I need to install a new 3 core 10mm? Or would 3 core 6mm just be ok?
thanks
Any cable calcs ?
 
If you assumed 40A as there is no diversity allowed for the hot tub, and you have little control over what else gets plugged into a 32A ring along with 4.4ish for the heater, then over 30m 6mm swa is OK but not great, 10mm is preferable for an energy conscious solution
 

Reply to Supply to garden room with hot tub in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock