Search the forum,

Discuss Supply to garden room with hot tub in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
There’s is currently a 3 core 6mm swa installed/40amp breaker, the garden room has its own consumer unit with a 32amp ring circuit and 6amp lighting.
The ring circuit has a 1kw heater and a computer/ printer so not a lot of load and the lights are led -total 60w.
They now want a 32amp hot tub supply.
do I need to install a new 3 core 10mm? Or would 3 core 6mm just be ok?
thanks
 
No mention of an RCD anywhere or what type of supply its on, TNS, TNCS, TT, length of cable run, a lot of details missing......
 

There’s is currently a 3 core 6mm swa installed/40amp breaker, the garden room has its own consumer unit with a 32amp ring circuit and 6amp lighting.
The ring circuit has a 1kw heater and a computer/ printer so not a lot of load and the lights are led -total 60w.
They now want a 32amp hot tub supply.
do I need to install a new 3 core 10mm? Or would 3 core 6mm just be ok?
thanks
Any cable calcs ?
 
If you assumed 40A as there is no diversity allowed for the hot tub, and you have little control over what else gets plugged into a 32A ring along with 4.4ish for the heater, then over 30m 6mm swa is OK but not great, 10mm is preferable for an energy conscious solution
 

Reply to Supply to garden room with hot tub in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
717
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
822
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
241

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock