Paul Willoughby

Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Who told you that?
 

Reply to Supplying garage with power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
187
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
899
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
406
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top