Paul Willoughby

Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Who told you that?
 

Reply to Supplying garage with power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
836
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
508
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock