Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?

2. BS7671 states 25mm to be used, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall?

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box?

Cheers chaps:biggrin:
 
Everything can given sufficient heat!
I'm not a scientist, but I think that when metal is heated to a sufficient temperature it changes from a solid state to a molten state. If it's heated to a higher temperature it may actually boil and turn into a gas. To catch fire, is a state of combustion. If metal can be combustible, then it's not gonna be much use as a material for 421.1.201. :)
 

Reply to SWA, T&E or tails?? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock