Morning guys!
Went to look at a consumer unit change today with a PME supply.
Now, right next to this was an old BS3036 60A fused mem cutout that then sent a pair of 16mm tails to the consumer unit up into the loft, across about 3m and then down the wall in surface trunking down to an old Crabtree CU, with a separate 16mm main earth along side.
Did a Z test at the CU and had a 0.45ohm result, but then the PME cutout had a Ze of 0.47?
I will call the DNO to make them aware, but from what i can see, a BS3036 fuse has an ELI max of 1.07ohms so as this is all well within the limits of the installation, so surely this is ok?
I have no plans to remove the MEM unit and replace with a new one as it is in excellent condition.